The minimum embedment depth of Hilti HAS-U threaded rod with HIT-HY 200-R V3 injection mortar

Posted by Jason Chewabout 2 years ago
The minimum embedment depth of Hilti HAS-U threaded rod with HIT-HY 200-R V3 injection mortar

Hi team,

I am currently proposing a base connection with Hilti HAS-U M10 threaded rod with HIT-HY 200-R V3 injection mortar. The tension & shear load (0.45kn & 1.185kN) is minor and it passed the design capacity based on the software and technical datasheet.

However, it seems like the minimum embedment depth needs to be minimum 60mm. My client insists to use 55mm embedment depth instead of 60mm. Could you please advice whether 55mm is applicable?

If not, do you have any better advice?

Regards,
Jason

Hilti 200-R,Minimum embedded depth

1 Reply
Posted by Mohammed Hamdounaabout 2 years ago
Hilti Verified

Hi Jason,

Thank you for contacting Hilti!

You are correct, the minimum embedment depth that was tested with HY 200-R V3 is 60mm, which is why Profis Engineering doesn't allow you to choose a shorter embedment depth, simply because we wouldn't have the data to support such a design.

Have you considered using a mechanical anchor option? We have multiple anchor options with different embedment depth requirements that might suit your application.

Please free to provide more information around your application requirement to be able to best support you with anchoring options.

Best regards,
Ask Hilti Team.