Seismic compliance with AS 1170.4

Posted by Frank Calvisiover 2 years ago
Seismic compliance with AS 1170.4

Hi, we are constructing a 7 level apartment building in Brisbane ( Type 2 construction, Earthquake design category 2 ). Can you please advise if your Hilti HUS 3 A and HUS 3 I fixings comply with AS 1170.4 when used for hanging plumbing drainage pipes from a concrete slab above.
A repose at your earliest possible convenience would be appreciated.

110mm wall,1.5 meters

1 Reply
Posted by Mariana Onetoover 2 years ago
Hilti Verified

Hi Frank,

Thank you for reaching out to Hilti.

For the design of post-installed anchors under seismic actions we suggest checking AS 5216:2021 Appendix F.

This appendix refers to AS 1170.4 and requires that fasteners for seismic actions shall be pre-qualified in accordance of the seismic performance categories C1 and C2 of EOTA TR049. Hilti has a range of mechanical and chemical anchors approved for seismic applications.

Please refer to tables C4 and C5 of the ETA-13/1038 (download here) for more information of the seismic performance of our HUS anchors.

Please reach out to our technical team for assistance to your specific projects >> link here.

I hope this is helpful.

Kind regards,
Ask Hilti team

HUS,seismic anchor

1 comment on this reply
Posted by Frank Calvisiover 2 years ago
Hi Mariana, when I go to your link to Tables C4 and C5 of ETA-13/1038 I simply get a blank screen. Is there some other way of accessing these tables ?