Posted by Charlie Wangover 4 years ago
Mr Charlie Wang

To stop smoke spreading to different levels, smoke seal between facade panels and slab edge is always required. Is the smoke seal to be 100% stopping smoke or certain leakage is allowed? Thank you.

Facade smoke seal,Leakage

1 Reply
Posted by Tony Yangover 4 years ago

Hi Charlie,

Thank you for your question,

For Edge of Slab seals, it is often referred to as the Leakage Rating. Keep in mind no arrangement including UL / ASTM can provide a 100% smoke free seal.
 
These are not measured in any percentage. The L Rating in UL Standards is measured as follows (highlighted)
 
ASTM E 2307 – which is for façade – has no criteria for L Rating – it is derived from ASTM E 1966 (for standard joints). The main thing to observe is that in Façade Firestop Testing that F Rating/ Integrity Rating is most important.

Australian Standards currently do not cover edge of slab seals however we have a lot of experience and data to lean on should you have further queries.

Please feel free to reach out with any further comments or questions here directly or through our Engineering/Technical Advise Services on www.hilti.com.au
 
Kind regards,

Ask Hilti Team
Australia

Firestop,edge of slab,seal