Posted by Matt Antounover 2 years ago
INFORMATION regarding HKD flush anchor
Need to know more information regarding hilti HKD flush anchor, are they good to use for fire rated cable tray??
- iv spoke with engineer from cable tray supplier and they suggest it is fire rated for non structural applications.
1 Reply
Posted by Mariana Onetoover 2 years ago
Hello Matt,
Thanks for reaching out to Hilti.
HKD anchors are fire approved and have been tested for up to 120 minutes. Please see the attached ETA for HKD anchors (Page 39, Table C5) which provides loading data at various fire resistance classes.
Hope this helps.
Kind Regards,
Ask Hilti Team