Chemical Anchors into TOP of core filled blockwork

Posted by Jonathan Watsonabout 3 years ago
Chemical Anchors into TOP of core filled blockwork

Is there a way in PROFIS to configure HIT anchors into the TOP of core filled blockwork?

HIT-HY 200R,HIT-HY270,HIT RE-500,Core-filled Blockwork

1 Reply
Posted by Mariana Onetoalmost 3 years ago

Hello Jonathan,

Thank you for reaching out to Hilti.

Unfortunately, we do not have any guidelines for installing anchors on top of core filled block work and hence cannot design such connection in Profis Engineering.

Given that there is no anchoring standard in Australia for masonry applications, Hilti follows the anchor installation guidelines given by “AEFAC TN 09 – Selection and Installation of Fasteners in Masonry” (link). It mentions that the anchors must be installed on the face of the brick. Our HIT HY 270 adhesive is commonly used in core filled block work application.

However, if you still choose to install anchors on top of the brick, we would suggest to perform on site testing to check the resistance of the anchor. If the anchor testing results are satisfactory and provides a truly safe anchor performance, then you can install your final anchors. Please note that this is just a suggestion and Hilti can not warranty or provide any design/ installation guidelines in such scenario.

Hope this helps.

Kind Regards,
Ask Hilti Team

HY 270,On site testing,masonry Anchoring