Anchor forced into connection

Posted by Kurt Jenningsalmost 4 years ago
Anchor forced into connection

We have a project where a sub-contractor has incorrectly located and installed the chemical anchors for a baseplate and had to force them approximately 15mm into position to fit the steel baseplate over. Will the anchor capacity be affected by this? I believe they may have forced them with a hammer. We are using RE-500 chemical anchors.

Chemical anchor,Straightness

1 Reply
Posted by Tony Yangalmost 4 years ago

Hi Kurt,

Thank you for your question. If the anchor bolt (threaded rod) has been bent to accommodate the plate position, there are a few things we need to be mindful of

  1. Potential damage to the anchors bond
  2. Bending on the threaded rod which may result in reduced capacities for steel failure modes


For further discussion specific to your situation, please reach out to our Anchor Design Team

Kind regards
Ask Hilti Team
Australia

Chemical anchor,bending